I have been automating some management network changes, namely breaking up a larger subnet/VLAN into much smaller subnets/VLANs. For this, I am using Python and the "HNMP" library to configure these settings on all the different types of radios we have in our network. I had a script that was working mostly well (Except for those pesky PMP320 CPEs...), though after a recent ePMP software update I noticed script would fail when it's setting the subnet mask and I would get an error that says "Bad Value".
After banging my head against the wall for way too long, I found that the issue was because there seems to be some added input validation on the subnet mask field that prevents you from making a silly mistake like changing the subnet mask to one that would put the default gateway outside the subnet. To work around this, I had to change the flow of my script that was previously:
(Set Management VLAN)
'.1.3.6.1.4.1.17713.21.3.4.4.2.0' = 100
(Set Subnet Mask)
'.1.3.6.1.4.1.17713.21.3.4.7.3.0' = '255.255.255.0'
(Set Default Gateway)
'.1.3.6.1.4.1.17713.21.3.4.7.4.0' = '10.0.0.254'
(Save Settings)
'.1.3.6.1.4.1.17713.21.4.3.0' = 1
(Apply Settings)
'.1.3.6.1.4.1.17713.21.4.4.0' = 1
After the changes, it flows like this:
'.1.3.6.1.4.1.17713.21.3.4.4.2.0' = 400
'.1.3.6.1.4.1.17713.21.3.4.7.4.0' = '10.4.0.254'
(Save Settings)
(Set Subnet Mask)
(Save Settings)
(Apply Settings)
So, you can't just change the default gateway first, you also have to change it, SAVE IT, then you're able to change the subnet mask.
I hope this helps someone else, I spent way too long trying to figure that out.